Hope I am posting the in the correct forum.

I need help to wire my 10 L3+ Antminers.

I would like a diagram that I can present to an electrician.

The farm will be setup up in my home in USA so 120v with standard 15 amp breakers.

The diagram should be scalable for when I inevitably add more miners.

I'm not opposed to adding bigger breakers, safety first efficiency second.

I will compensate you with BTC for the diagram if it is legit.

Thanks in advance.




here you go  you want 2x   30 amp  240 volt  put in

use 10 gauge wire  use 2 pole breakers.

have two l6 30r one for each circuit


http://www.ebay.com/itm/NEMA-L6-30R-Turn-Twist-Lock-Locking-Receptacle-Outlet-30A-250V-2P-3W-L6-30-/162134424426?


use 2 pdu's  each has 4 plugs and can do 24 x 240 volts =

http://www.ebay.com/itm/HP-Hewlett-Packard-228481-002-Module-PDU-Control-Unit-200-240VAC/261469140311?

  use a few of these on each pdu
http://www.ebay.com/itm/HP-modular-PDU-extension-bar-p-n-228480-002-BEST-PRICE/272270265827?


lastly get some of these


http://www.ebay.com/itm/LOT-of-20-IEC-C13-to-C14-jumper-cord-cable-5-ft-length-/232389461182?



1 30 amp circuit breaker to 1 30 amp  receptacle to  1 24 amp pdu to 2  breakout extensions   to   your  6 power cords

do this one time  for 6x   800 watt l3's
do this two time for 12x  800  watt l3's

if you want to send me coin  here is an ltc address